[Beowulf] Re: Emergency Power Off
Jim Lux
James.P.Lux at jpl.nasa.gov
Tue Mar 20 14:07:43 PDT 2007
At 01:25 PM 3/20/2007, David Mathog wrote:
> > At 04:20 PM 3/19/2007, David Mathog wrote:
>
>On further consideration, that common ground might be
>a problem. On the one hand it's effectively running from one
>serial port to another and generally that's ok. On the other
>hand, if for whatever reason one or more of the grounds is
>a volt or two higher than another one, that could result
>in quite a current running on that signal wire. This would
>probably be safer:
or use diodes. e.g. 1n5711 or 1N5401
Given that there is probably an alternate grounding path, you
probably want two diodes for each UPS (one in each line).
or, get a switch with 5 sets of contacts and use 5 sets of batteries
(I assume you were using Alkaline 9V batteries?)
James Lux, P.E.
Spacecraft Radio Frequency Subsystems Group
Flight Communications Systems Section
Jet Propulsion Laboratory, Mail Stop 161-213
4800 Oak Grove Drive
Pasadena CA 91109
tel: (818)354-2075
fax: (818)393-6875
More information about the Beowulf
mailing list